    ERR 40 Overload on 1 hp VFD Running 0.75 hp Motor

    2 months ago
    #549 Quote
    Hello everyone,

    I’m trying to get these drives to work with my motors, but having no luck. I’ve changed some parameters in the 1 hp VFD (Model: EM15-SP1S1-d75), but the motor shaft only shakes slightly when I try to run it. The drive sounds normal, but it doesn’t seem to have enough power to turn the shaft.

    I did check, and the pump shaft turns freely by hand. I’m sending a 0–10 V signal on AI1 and using DI1 for start/stop. Has anyone run into this before, and could you share the correct parameters to get these motors running?
    1
    2 months ago
    #550 Quote
    Leocadia wrote:
    Hello everyone,

    I’m trying to get these drives to work with my motors, but having no luck. I’ve changed some parameters in the 1 hp VFD (Model: EM15-SP1S1-d75), but the motor shaft only shakes slightly when I try to run it. The drive sounds normal, but it doesn’t seem to have enough power to turn the shaft.

    I did check, and the pump shaft turns freely by hand. I’m sending a 0–10 V signal on AI1 and using DI1 for start/stop. Has anyone run into this before, and could you share the correct parameters to get these motors running?
    Hi Leocadia,
    The ERR 40 fault is an overload error. Your 0.75HP (0.55kW) single-phase motor has a rated current of 5.3–5.86A at 230V, while the VFD model you purchased (EM15-SP1S1-d75, 0.75kW) only supports 4A rated current. Since the motor current rating is higher than the VFD’s capacity, this leads to overload.
    Usually, the capacity of the VFD is greater than the capacity of the motor, so we recommend a 3 hp VFD to match your motor. Please see spec on: https://www.ato.com/3hp-vfd-single-phase-120v-input-1-phase-3-phase-220v-output
    1
    ATO.com
    2 months ago
    #551 Quote
    Thanks for the quick reply. I didn’t expect this to be an amp issue since the VFD was showing 13A before it tripped with ERR 40.
    1
    one month ago
    #552 Quote
    Leocadia, I ran into something similar with a 1 HP pump motor. Even though the motor plate said 5A, the startup current was way higher. A small VFD tripped every time. I ended up going with a bigger drive (2x motor capacity), and it worked fine. I’d suggest trying the same.
    2
    one month ago
    #553 Quote
    Leocadia wrote:
    Thanks for the quick reply. I didn’t expect this to be an amp issue since the VFD was showing 13A before it tripped with ERR 40.
    Since your motor’s rated current is already greater than the rated current of the VFD, the overload trip is expected. You may send us a video for further confirmation.
    As a test, disconnect the motor from the VFD and check if the drive runs normally with no load. If it does, then the issue is simply that the motor draws too much current and the VFD cannot start it properly.
    1
    ATO.com
    one month ago
    #554 Quote
    Hi, I'd like to say that before buying a bigger drive, double-check your parameter setup. Make sure the motor parameters (rated voltage, frequency, current, power) are entered correctly into the VFD. Also, look at the acceleration time—if it’s too short, the VFD might trip on overload during startup. Sometimes, just extending the ramp-up time fixes the shaking issue.
    1
    one month ago
    #555 Quote
    Appreciate all the feedback! I’ll first try adjusting the parameters and ramp-up, and if that doesn’t solve it, I’ll move up to a larger VFD as suggested.
    0