Zephyrine wrote:We are getting the error when bench testing the unit with a pressure regulator. We seem to be getting the error when the pressure received from the sensor doesn’t reach the sleep pressure in the amount of time of P6.42 (Constant pressure water supply blockage judgment time)
This will likely not be an issue once we have the pump integrated into the system, as the pressure will reach the sleep frequency before the P6.42 timer runs out. Is there a way to turn off P6.42?
The VFD is showing it is running at the maximum Hz, so I don’t think the motor frequency is lower than the sleep frequency during constant pressure water supply.
P6 settings are listed below.
P6. 00 2 22 0
01 50 23 1
02 1 24 1
03 0 25 0
04 1 26 0
05 5 27 0
06 2 28 0
07 0 29 0
08 0 30 0.5
09 0 31 1
10 0.1 32 0.005
11 0 33 1.2
12 0 34 0.001
13 0 35 0.8
14 0 36 2
15 20 37 1
16 2 38 5
17 0 39 25
18 0 40 10
19 20 41 01
20 80 42 60
21 0
I have looked through this information, and have questions regarding P6.00, P6.01, P6.30.
P6.00=0. What does PID given mean? Are we telling the VFD what the pressure is? I understand this is a selection for using P6.01 setting as the source.
P6.01=50. Is the VFD trying to target 50% of the range? How does this affect the VFD logic?
P6.30=0.7. How does this given pressure affect the VFD logic?
Currently, the VFD is sending out maximum motor frequency when the pressure is lower than the sleep pressure level (P6.37). Once the sleep pressure level (P6.37)is reached, the frequency starts to drop after the sleep pressure level continuous time (P6.38). The pressure drops to Awakening pressure level (P6.35), and after Wake-up pressure level continuous time (P6.36) the VFD motor frequency starts to climb again. Is this how it is intended to operate? Constantly cycling between the sleep pressure level (P3.37) and awakening pressure level (P6.35)? Based on this, the VFD seems to be targeting the sleep pressure level at all times, and not the given pressure (6.30), correct?
Zephyrine,
1.P6.05 can be adjusted by itself; the factory default is 20. It is the proportional gain Kp1, which determines the adjustment intensity of the entire PID regulator. The larger Kp1, the greater the adjustment intensity.
2. P6.08 is the PID reversal cutoff frequency; there is no need to set this parameter. You can just use the factory default value = 2.00; it will not cause inversion.
3. P6.27 PID feedback loss detection time can be set to 0, or the factory default value = 1 can be used. This does not affect use; you do not need to set it.
4. You can increase the pressure value of P6.33 by yourself.
5. P6.34 = 0.01 – We set this value to 0.001 to minimize alarms, but may increase this value closer to 0.7MPa in the future to account for pressure loss alarms.——OK, you can set it like this.
6. P6.41=00 This is the correct setting. The sleep pressure and sleep frequency must be reached at the same time to be effective, and the wake-up sleep pressure is the actual pressure.
7. You should set P0.01=10, which sets the VFD to constant pressure water supply mode.
P0.01=8 is the PID given; we set P6.01 to be also the PID given. In the constant pressure water supply mode, P6.01 is equivalent to P0.01=8.