    VFD Showing E-03 Overcurrent When Using Motor Controller

    14 hours ago
    #1071 Quote
    Hello, I have installed one of the ATO GK3000-1S0022G drives to run an 8.7 amp 1 phase motor, and I can’t get it to work. It keeps showing E-3 on the display. I’d appreciate any guidance on how to troubleshoot this.
    0
    12 hours ago
    #1075 Quote
    vivi wrote:
    Hello, I have installed one of the ATO GK3000-1S0022G drives to run an 8.7 amp 1 phase motor, and I can’t get it to work. It keeps showing E-3 on the display. I’d appreciate any guidance on how to troubleshoot this.
    You can try troubleshooting on your own. E-03 is “running over current at constant speed.” The possible reasons and solutions are listed in the table below.
    1
    ATO.com
    9 hours ago
    #1086 Quote
    vivi wrote:
    Hello, I have installed one of the ATO GK3000-1S0022G drives to run an 8.7 amp 1 phase motor, and I can’t get it to work. It keeps showing E-3 on the display. I’d appreciate any guidance on how to troubleshoot this.
    E-03 on most VFDs usually means overcurrent during operation. A couple of quick things to check: Is your motor wired correctly for the voltage? Any sudden load or mechanical binding? Acceleration time too short can also trigger this
    Also, are you running the motor directly from the VFD or is there anything in between?
    0
    9 hours ago
    #1087 Quote
    Impellizzeri wrote:
    Hello, I have installed one of the ATO GK3000-1S0022G drives to run an 8.7 amp 1 phase motor, and I can’t get it to work. It keeps showing E-3 on the display. I’d appreciate any guidance on how to troubleshoot this.E-03 on most VFDs usually means overcurrent during operation. A couple of quick things to check: Is your motor wired correctly for the voltage? Any sudden load or mechanical binding? Acceleration time too short can also trigger this
    Also, are you running the motor directly from the VFD or is there anything in between?
    Thanks for the suggestions. The wiring should be correct, and there’s no mechanical load at the moment. However, we are not running the motor directly from the VFD—there is a motor controller between them.
    0
    9 hours ago
    #1088 Quote
    ATO wrote:
    Hello, I have installed one of the ATO GK3000-1S0022G drives to run an 8.7 amp 1 phase motor, and I can’t get it to work. It keeps showing E-3 on the display. I’d appreciate any guidance on how to troubleshoot this.You can try troubleshooting on your own. E-03 is “running over current at constant speed.” The possible reasons and solutions are listed in the table below.
    Hello, our motor is 2kW, 230V, 60Hz single phase. But we are not directly connected to the motor. We have a 230V 50Hz power supply to the drive, then out of the drive 230V 60Hz to the motor controller, then out to the motor. I have the drive outputting 230V 60Hz, but as soon as I press start on the motor controller, it gives the E-03 fault code.
    1
    8 hours ago
    #1092 Quote
    vivi wrote:
    Hello, our motor is 2kW, 230V, 60Hz single phase. But we are not directly connected to the motor. We have a 230V 50Hz power supply to the drive, then out of the drive 230V 60Hz to the motor controller, then out to the motor. I have the drive outputting 230V 60Hz, but as soon as I press start on the motor controller, it gives the E-03 fault code.
    That setup is likely your problem. VFDs are designed to drive motors directly, not another controller. When you put a motor controller between the VFD and the motor, it can look like a non-linear or reactive load, which can easily trigger overcurrent faults. Basically, the VFD expects a motor (inductive load), not electronics in between.
    0
    8 hours ago
    #1093 Quote
    vivi wrote:
    Hello, our motor is 2kW, 230V, 60Hz single phase. But we are not directly connected to the motor. We have a 230V 50Hz power supply to the drive, then out of the drive 230V 60Hz to the motor controller, then out to the motor. I have the drive outputting 230V 60Hz, but as soon as I press start on the motor controller, it gives the E-03 fault code.
    The product you purchased is GK3000-1S0022.
    The controller between the motor and the VFD may cause the E-03 fault. The VFD accepts only motor-type loads, so there should be no lights, circuit boards, or other devices between the controller and the VFD.
    0